Reading a Mike Holt article, he says regarding the 2011 NEC and article 645... "The change to this Note makes it clear that Art. 645 applies only if the room is constructed per NFPA 75, Standard for the Protection of Information Technology Equipment. So when must you comply with NFPA 75? Only when you want to reap the benefits allowed by Art. 645."
So is the takeaway message that if the room is not built to NFPA 75 standards then it is not considered an IT room according to the NEC? Meaning no requirement that a disconnect be installed at the exit that would power off all IT equipment and HVAC equipment serving the room?