IT Stubs

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
So the room where these devices are has exposed ceiling which would require cabling to be enclosed in raceway but there is a hung ceiling in the corridor where the cable tray is. I'm thinking I could stay in the wall(unitl I rise up by the corridor wall) for the three devices(on same wall) but my question is the conduit. Usually IT outlets have individual stub ups to the accessible ceiling.

In this instance would you connect the IT devices with a common raceway( to be sized properly based on cable qty) as you would if wiring receptacles or would run separate conduits from each device to the tray? Thanks.


1701869600129.png
 
You could combine them but the plans usually require one stub for each drop. I would write an RFI asking this question to the owner or engineer. This way you are covered. It would suck trying to fix it later...
 