So the room where these devices are has exposed ceiling which would require cabling to be enclosed in raceway but there is a hung ceiling in the corridor where the cable tray is. I'm thinking I could stay in the wall(unitl I rise up by the corridor wall) for the three devices(on same wall) but my question is the conduit. Usually IT outlets have individual stub ups to the accessible ceiling.
In this instance would you connect the IT devices with a common raceway( to be sized properly based on cable qty) as you would if wiring receptacles or would run separate conduits from each device to the tray? Thanks.