rhamblin
Senior Member
- Location
- Kaukauna, Wisconsin
I need to run four circuits for a break room we are remodelling at work. I want to clarify something, that a coworker disagreed with, and I want to make sure I am understanding correctly. I would like to pull (4) 120 volt circuits into a conduit to feed recepts in the walls. Now if i run 4 circuits (4 hots and 4 neutrals), and 1 ground wire; I have to derate to 70% right (T310.15(B)(3)(a)? But and here is the question, that derating can come off the maximum ampacity in T310.15(B)(16), correct? Since I will be pulling THHN wire into the conduit. I can derate 70% of the 30 amp rated #12 AWG (again using the maximum 90°C column, right? So this derating puts me down to 21 amps, of which I can only use 20 amps because of termination limitations (75°C column).
Am I remembering this correctly?
Am I remembering this correctly?