Is it me or are most of those #12 terminated on 30A breakers?
The Emt connectors do not line up.J/K
Double noodles in the buss.
I don't think two grounded conductors under one terminal has ever been compliant. It was part of the listing instructions. The only reason it is now in the code is because installers were not reading the label on the panel.Double wires on breakers and neutral bar although the 2 wires under one lug for the neutral may have been compliant when it was installed. White wire used as a hot may not be taped.
Is there a neutral feeding the panel? Don't know if I'm not seeing or it or if it's not there.
Also, can somebody explain to me the 4-pole main breaker?
On a picky violation note, my guess is that panel is rated for that many double breakers to go with all those full size breakers.
Look to the right side of the Main Breaker and you'll see a white taped full sized current carrying conductor landing on the top lug of the right hand neutral bus.Is there a neutral feeding the panel?
Awesome emoticon.It's Friday!![]()
Okay so we have our usual mish mash of breakers, and double taps, but what else? I dunno.Time for Spot the Violations!
Awesome emoticon.
I got a million of 'em.![]()
Where is this panel located. I'm guessing it is a house. If that's true, what is up with all the EMT?
It's in a dwelling. EMT is allowed in dwellings, isn't it?
Yes, but it's listed as EEW.It's in a dwelling. EMT is allowed in dwellings, isn't it?