Fire Department: 200A split phase (single phase) and a 200A 120v 3-phase service.
Fire department want both to run off same generator as currently they have 2 but one always causes issues.
??? Not worrying about the load; if one connects both transfer switches to one generator, could the neutrals of both services be bonded or would one end need a transfer switch that switches the neutrals from it's service to the generator's???
I would say not, in that service neutrals must remain separate. If you ever lost one neutral on the service it would overload the other. This could also be a hazard to linemen.
Any idea on NEC? :?
Fire department want both to run off same generator as currently they have 2 but one always causes issues.
??? Not worrying about the load; if one connects both transfer switches to one generator, could the neutrals of both services be bonded or would one end need a transfer switch that switches the neutrals from it's service to the generator's???
I would say not, in that service neutrals must remain separate. If you ever lost one neutral on the service it would overload the other. This could also be a hazard to linemen.
Any idea on NEC? :?