J boxes and mounting receptacles or light fixtures from them.

Status
Not open for further replies.

2xcheck

Member
Location
Ohio
Occupation
Maintenance electrician
Hey guys got a job to install power for block heaters for diesel trucks. I have 2 inch rigid underground coming to each of the 5 areas . I'm going to mount a jbox and use the rigid as its supports. The question i have is can I then mount a light or receptacles or an additional j box on top of the 1 that has the pipe supports. So its a 12x12x6 j box mounted to 2 runs of 2inch rigid . I would like to mount right of this j box but not sure if it allowed not really understanding the codes on this. Thanks in advanced
 
What you are proposing is not code compliant even without the extra light and/or box. See 314.23 (F). Also wondering how many conductors are in that 2" conduit as it sounds like derating may be required.
 
2 number 4s and 1 number 6 ground .
And 1 #12 circuit for a light on each station .
 
There are a few options as far as mounting your receptacles but as Texie notes using the 2" conduit as sole support is a violation.
 
Post 3 raised some additional red flags. Depending on your conduit entries with a #4 conductor a 12x12 box may not meet the requirements of 314.28. Once you broach those problems it sounds s if you will need to mount individual overcurrent protection panel and receptacle boxes to your larger j box. To assure the install meets Code you might want to get help from a professional.
 
It's a u pull.
That still may not be big enough, many apply the 2nd to the last paragraph in 314.28(A)(2) even where the conductors are being spliced.
314.28(A)(2) ... The distance between raceway entries enclosing the same conductor shall not be less than six times the metric designator (trade size) of the larger raceway. ...
Note that the code language is not really clear, as it is not really the same physical conductor if the conductor is spliced.

As far as the original question, provide independent support for the box, install a power distribution block, and branch circuit fuses in the box, cut the receptacles into the box cover and install bubble covers.
 