Well maybe I need to understand this code a little better. I always thought it had to be on its own circuit and a GFCI readily available and within 6 ft horizontally. It was thinking this 6 ft made it obvious what it was used for (Jacuzzi bath). But now I am wondering if they are only resaying what we already know as the 6' GFCI receptacle rule for dwelling water sources in 210.8(A)(7)?
680.71 Protection. Hydromassage bathtubs and their associ-
ated electrical components shall be on an individual branch
circuit(s) and protected by a readily accessible ground-fault
circuit interrupter. All 125-volt, single-phase receptacles not
exceeding 30 amperes and located within 1.83 m (6 ft) mea-
sured horizontally of the inside walls of a hydromassage tub
shall be protected by a ground-fault circuit interrupter.