Jail Smoke Purge System - Emergency or Stand-by Power

Status
Not open for further replies.

mjf22

New member
Location
Texas
Is a smoke purge system for a jail facility considered an Emergency, Legally Required Stand-by, or Stand-by system (NEC Articles 700, 701, 702)? References?
 

GrayHair

Senior Member
Location
Nashville, TN
My first instinct was that it's Life Safety and would fall under 700. However, 701.2 (2014 NEC) Informational Note lists "ventilation and smoke removal systems" so I guess it falls there. As usual, the AHJ is the final arbiter.
 