I have an apartment building I will be increasing the size of the service. There are no house loads on this service, only apartments. The existing service is 3PH, 120/208V, 1200 amps. I will be going up to 1600 amps. The existing 3 1/2" PVC conduit is big enough to install the larger wires needed to increase ampacity.
Since the conduits are PVC, I am permitted to run a single phase in each of the conduits. Eg. all phase A wires in one conduit, ditto for phases B & C. Each conduit will also have a neutral conductor, which is not a current carrying conductor.
Each phase will have 8 paralleled wires derated to 70% (Table 310.15(B)(2)(a)). Do I have to derate the non current carrying neutral in the same conduit to 70% also?
Thanks,
Jim
Since the conduits are PVC, I am permitted to run a single phase in each of the conduits. Eg. all phase A wires in one conduit, ditto for phases B & C. Each conduit will also have a neutral conductor, which is not a current carrying conductor.
Each phase will have 8 paralleled wires derated to 70% (Table 310.15(B)(2)(a)). Do I have to derate the non current carrying neutral in the same conduit to 70% also?