transman2
Senior Member
- Location
- Brooklet,Ga.
Ok, lets see if I got this right. If the electrode grounding conductor is terminated in the meter and there is a metal raceway between the meter and the main service disconnect you do not bond the grounded (neutral) bar via green screw or bond jumper to grounding terminal strip in the main service disconnect.
But, if there is a PVC raceway you do bond the grounded (neutral) bar via green screw or bond jumper to grounding terminal strip in the main service disconnect. Is that correct?
This seems confusing sometimes since you always here electricians say you must connect the grounded and grounding bar together at the first means of disconnect and then keep them separated at all panels afterwards.
But, if there is a PVC raceway you do bond the grounded (neutral) bar via green screw or bond jumper to grounding terminal strip in the main service disconnect. Is that correct?
This seems confusing sometimes since you always here electricians say you must connect the grounded and grounding bar together at the first means of disconnect and then keep them separated at all panels afterwards.