Sorry to post another "fire pump" thread as my search pulled up quite a few, none specifically concerning my situation.
At a golf course, a fire pump for a new club house was added to an existing seperate structure, the irrigation/main pump house. This building has a 400a 480V 3ph. service. At some point, someone replaced the meter on said building with a j-box (meter was relocated to utility xfmr pad) and added a 2nd 400a fused disconnect on outside of building for the fire pump. (Hope I'm not rambling) Out of this disco we are now feeding the fire pump controller (480v, 50hp motor) and jockey pump/controller (installed as 240V, single phase). My boss already gave a price on this job/blah blah so I'm just here to do it, but we are basically tapping off the fire pump controller feed (3/0) to feed a 480V pri./240V sec. 5kva transformer, whose only load will be the 3/4hp jockey pump/controller.
My question is, do I treat this transformer as a firepump transformer per 695.5 (B) for fusing the primary and NOT fusing the secondary? Or because it's only for the jockey pump (695.1 (B) (2)) do I fuse the primary and secondary as if it were any other water pump/load?
At a golf course, a fire pump for a new club house was added to an existing seperate structure, the irrigation/main pump house. This building has a 400a 480V 3ph. service. At some point, someone replaced the meter on said building with a j-box (meter was relocated to utility xfmr pad) and added a 2nd 400a fused disconnect on outside of building for the fire pump. (Hope I'm not rambling) Out of this disco we are now feeding the fire pump controller (480v, 50hp motor) and jockey pump/controller (installed as 240V, single phase). My boss already gave a price on this job/blah blah so I'm just here to do it, but we are basically tapping off the fire pump controller feed (3/0) to feed a 480V pri./240V sec. 5kva transformer, whose only load will be the 3/4hp jockey pump/controller.
My question is, do I treat this transformer as a firepump transformer per 695.5 (B) for fusing the primary and NOT fusing the secondary? Or because it's only for the jockey pump (695.1 (B) (2)) do I fuse the primary and secondary as if it were any other water pump/load?