raider1 Senior Member Staff member Location Logan, Utah Jan 22, 2010 #2 Are you asking in regards to the Tables in Article 310? Chris
J John J Stewart Member Jan 25, 2010 #3 raider1 said: Are you asking in regards to the Tables in Article 310? Chris Click to expand... Yes as to tables in 310
raider1 said: Are you asking in regards to the Tables in Article 310? Chris Click to expand... Yes as to tables in 310
raider1 Senior Member Staff member Location Logan, Utah Jan 25, 2010 #4 Conductors installed in a raceway or cable would not be considered to be in free air. Open wiring on insulators (Article 398) would be an example of conductors in free air. Chris
Conductors installed in a raceway or cable would not be considered to be in free air. Open wiring on insulators (Article 398) would be an example of conductors in free air. Chris