Re: joules
Dereckbc:
For some reason I couldnt D/L the info you pasted.
I however did check as many Tvss strips as I could find, and the majority listed UL 1499 and some listed 1497 as the Eval. standard.
I believe we are on the same track here since Energy is what this field is all about. We install a 200 amp service in lieu of saying a 48kva system.
To say that these strips do NOT absorb energy is incorrect, the joule rating is used on a short term basis.
Spikes, transients , surges are short duration, and yes you are correct it will problably be toast when all is said and done.
The more expensive models had a lifetime guarantee, as I said above, but as you have already noted they smoke which is the case.
Spikes and surges are notorious for going through transformers be it lightning or a line abnormality. case in point, Isolation transformers do not protect SCR drives as once believed, drive paks will smoke real quick and the isolation transformer will just carry the spike right through to the scr pak and totally wipe it out. When this first happened, the first to see was the huge MOVs totally blown apart, and of course the first thought was. " Great they did their job, unfortunately, upon closer inspection the whole board was toast.
The 'amps per mode' is understandable, but with out a voltage pushing it, it means little. and hence the power associated with it, however, short the duration.
WOC