Jouneymans exam question
Section 110.14(C)(1)(a) is very clear and states conductors 14 through 1 AWG will be sized off the 600 F Colum and you may use a deferent insulation rating, provided the ampacity of such conductors is determined based on the 60?C (140?F) ampacity of the conductor size used.
Table 310.16 ampacity are based on the terminal rating. Regardless ampacity rating based the insulation type of the conductor; the ampacity of the conductor is solely based on the terminal rating, so with out the terminal rating we will need to assume the terminal rating to be 600. The question does not gave the terminal rating even if the NEC does permit the use of higher ampacity rated conductor it is clear that the terminal is what the ampacity of the conductor will be based on.
110.14(C) Temperature Limitations The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
(1) Equipment Provisions The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or (C)(1)(b). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.15(B)(6).
(a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following:
(1) Conductors rated 60?C (140?F).
(2) Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60?C (140?F) ampacity of the conductor size used.
(3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors.
(4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75?C (167?F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75?C (167?F) ampacity.