Hi All,

I've have a customer of mine who has a JuiceBox 40 that he needs wired. It's a hardwired version that has three #6 finely stranded Cu conductors. I'm having trouble finding wire connectors that are rated for finely stranded to 6/2 NMB wiring. I've called both the manufacturer of the unit and Polaris connectors. Both were unable to assist or advice me to a listed wire connector. Has anyone ever hardwired one of these units before? If so what means of connection did you use? I was thinking about using a Polaris Grey connector if I can't find the correct solution. I asked to speak to the engendering department of the charger to find out exactly what the wire type is but I never heard back from anyone.

https://evcharging.enelx.com/ca/en/store/residential/juicebox-40
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't see the fine line between "Stationary Equipment" {645.44(B)| and "Fixed Equipment" {645.44(C)} but it seems odd that they even offer a "hardwired" unit. The grey polaris connectors seem to fit the bill for you.
 