Re: Jumping the water meter.
Good Morning George I had to step out and get some stocking stuffers.
Originally posted by georgestolz:
But it is missing the supplemental GEC, isn't it?
There is no such thing as a supplemental GEC.
There is a requirement for a Supplemental Electrode. 250.53(D)(2)
The only time this requirement is an issue is when the water pipe is the only electrode available.
If the water pipe is the only available electrode you must install a Supplemental Electrode, however nothing says that has to be a rod, it could be any type of electrode.
Originally posted by georgestolz:
Doesn't that have to go to the service?
If you are asking about the conductor running to the Supplemental Electrode no, it does not have to go to the panel it can go to the panel or to an other part of the grounding electrode system.
Originally posted by georgestolz:
The size of the GEC is determined by 250.66, but what determines the size of all the jumpers? Can you cite a code reference?
250.53(C) tells us how to install the bonding jumpers per 250.64(A) and size them per 250.66.
Now 250.66 tells us how to size GEC and the bonding jumpers to Table 250.66 but.....
250.53(E) tells us no mater what the bonding jumper to Supplemental Electrode is a rod, pipe, or plate electrode the bonding jumper does not have to be larger than 6 CU or 4 AL AWG.
250.66(A) tells us Rod, Pipe, or Plate Electrodes only need 6 CU or 4 AL AWG.
250.66(B) tells us Concrete-Encased Electrodes only need 4 CU
250.66(C) tells us Ground Rings do not need conductors larger than the ring itself.
I will be installing a 600 amp 480 volt temporary service next week, I have not seen the site yet but it is very likely all I will have is two ground rods as my grounding electrodes, the GEC from the 600 amp disconnect to the ground rods will only be 6 AWG.
I could just put one ground rod in if I could prove 25 ohms or less resistance but it is just easer to install a second rod. Check out 250.56 for this requirement.
I have not decided what I will be running to the service probably 3 runs of 4/0 AL. That being the case if a water pipe is available that conductor would need to be 1/0 CU.