junction box access

Status
Not open for further replies.
Re: junction box access

what about 410.14 (A) ?

Talking about fixtures supported by a ceiling grid and the such... where the fixture does not lay against the ceiling surface.
 
Re: junction box access

I only see that it refers to fixtures not supported by the outlet box.
 
Re: junction box access

Which would be fluorescents in a ceiling grid,or fixtures supported by jack chain . They would not supported by "a box" but hooked up like 410.14 (A) says they can be.
 
Re: junction box access

Look....you asked what about 410.14 (A)?

I tried to show examples of where this article applies..thats all.

And NO I am not talking about 410.16 (c) thats a different issue than the original question about boxes, access and fixtures independent of outlet boxes....
 
Re: junction box access

What is the difference between mounting the surface mount florescent fixture and a regular ol' incandescent fixture at the box? In either case, you have to remove the fixture to get to the box.

oh... luminaire... sorry.
 
Re: junction box access

If you use A 3" knockout in the back of the flo. fixture where the box is you have acsess to the box when you have the fixure fastened to the ceiling.

The hole is covered by the ballast cover and you still meet the requirements of 410.14(B) ,plus they are easy to install this way.
 
Re: junction box access

Let me start over and be more specific about what I meant with my question.

Does anybody think it might be possible to apply either 410.14(A) or 410.14(B)to the same situation?

If you can, and it looks like you can to me, then 410.14(A) and 410.14(B) conflict with each other.
 
Re: junction box access

Looks like you're right. 410.14(A) applies to 410.30(B) & (C) and screwing a fixture to the ceiling isn't in those sections.
 
Re: junction box access

This is a related question. Is anyone else uncomfortable with the sharp sheet metal edges on some fixtures (primarily vanity lights for bathrooms). They are manufactured with a large hole for access to the wiring in the box, but it seems like they should include a plastic grommet to protect the wires from the sheet metal. Just my opinion, I guess UL has listed them this way.

Mark
 
Re: junction box access

I get concerned about that too. Sometimes I'll slide some sheathing over the conductors passing through the hole, or drill my own with a unibit and install a grommet.

Related related question: Where can I find if certain vanities (with backplates) can be used as the junction box?
 
Re: junction box access

So you guys are saying that I can punch a say 2 or 3 inch hole for access then mount over the JB? Does this violate the manufacturers or UL listing? Comments?
 
Re: junction box access

First, a lot of fixtures have a KO for this. And second, cutting a messy hole is pretty common but I don't think it's ok either.
 