This is the code section I was referencing. I don't know if there is a jbox restriction in the NEC, but it seems logical based on this. At minimum, IMHO, the jbox and cover should be wet rated.
410.10 Luminaires in Specific Locations.
(D) Bathtub and Shower Areas. No parts of cord connected
luminaires, chain-, cable-, or cord-suspended luminaires,
lighting track, pendants, or ceiling-suspended (paddle)
fans shall be located within a zone measured 900 mm (3 ft)
horizontally and 2.5 m (8 ft) vertically from the top of the
bathtub rim or shower stall threshold. This zone is all encompassing
and includes the space directly over the tub or shower
stall. Luminaires located within the actual outside dimension
of the bathtub or shower to a height of 2.5 m (8 ft) vertically
from the top of the bathtub rim or shower threshold shall be
marked for damp locations, or marked for wet locations where
subject to shower spray.
This is got me thinking once.
In reguard to exhaust fans or fixtures which the NEC says nothing about GFCI protection for but manufacturers do, is that typically in the the instructions wil says above tub/shower. Do you think that the instructions follow the footprint as defined in NEC or do you think more as the true footprint proper of the tub or shower?