A anbm Senior Member Location TX Occupation Designer Jan 19, 2024 #1 Are conduit and j-box marked with circuit numbers required by code or just because of engineering specification?
Are conduit and j-box marked with circuit numbers required by code or just because of engineering specification?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jan 19, 2024 #2 Not required by the NEC for normal branch circuits. Emergency circuits boxes are required to indicate an emergency system.
Not required by the NEC for normal branch circuits. Emergency circuits boxes are required to indicate an emergency system.
T tank728 Senior Member Location New Jersey Occupation Electrician Jan 19, 2024 #3 infinity said: Emergency circuits boxes are required to indicate an emergency system. Click to expand... What code section might that be?
infinity said: Emergency circuits boxes are required to indicate an emergency system. Click to expand... What code section might that be?
R rc/retired Senior Member Location Bellvue, Colorado Occupation Master Electrician/Inspector retired Jan 19, 2024 #4 tank728 said: What code section might that be? Click to expand... 700.10(A)
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jan 19, 2024 #5 Not required but really usefull over the life of the building. Easy to do with a sharpie
roger Moderator Staff member Location Fl Occupation Retired Electrician Jan 19, 2024 #6 There are also requirements in 517 for critical branch circuits.