Is metallic one gang junction box (like sigma box) used as a conduit body to help pulling wires straight through EMT conduit required to be grounded?
The J box has a green ground screw for grounding conductor. Can I run my ground wire (like the hot and neutral ) straight through without having to cut the ground wire and then spice with a pigtail wire from the ground screw? Thanks.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
See 250.148.

As long as the box is bonded via the EMT anyway, you are only required to bond the redundant wire-type EGC to the box if you are otherwise splicing conductors in the box.

Cheers, Wayne
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree the box is grounded via the emt. If you don't trust the emt then you could just strip a small section and install a short piece of wire to ground using a split bolt connector
 

SKSolar

Member
Location
Los Angeles
Occupation
Engineer
Thank you Sirs. Great. I just read 250.148 and it talks about splicing conductors in the box which I am not. My terminal J Boxes are to be grounded to the Green screw. I am only afraid that the Inspector would want me to ground the pull J box and then I don't have enough length to make the splicing. In that case, I shall leave a small loop length for the ground wire in the J box so that I can use a split bolt connector to ground it when The Inspector required it as Dennis suggested.
 