jeff48356
Senior Member
- Location
- Livonia, Michigan
I'm running a 60A feeder for power out to a detached garage, with additional wiring for a 3-way switch for the outdoor lights on it. The junction box in the basement where it connects to the 1" PVC conduit to go to the garage would need 44.5 cubic inches to hold 6 #6 conductors, 3 #14's for the 3-way switch, and a #10 ground that counts as all one conductor.
The question is, since the #14's are two travelers and a common, would I be able to eliminate two of them (one of the THWN's in the conduit and one in the Romex) from the count since only one traveler can carry current at any given time? If so, I would only need to count both travelers as one conductor, plus the common. That would bring it down to 40.5 cubic inches, where a 4-11/16" square box is rated for 42 cubic inches.
If not, what's the next size up in junction boxes that I could use?
The question is, since the #14's are two travelers and a common, would I be able to eliminate two of them (one of the THWN's in the conduit and one in the Romex) from the count since only one traveler can carry current at any given time? If so, I would only need to count both travelers as one conductor, plus the common. That would bring it down to 40.5 cubic inches, where a 4-11/16" square box is rated for 42 cubic inches.
If not, what's the next size up in junction boxes that I could use?