Re: Junction Box Full
Assuming you mean 3R enclosure (raintight), All conductors being larger than #4 AWG, 314.28(A)(2) tells us for angle pulls (again assumed), we need 6 times the trade size, plus the sum of the diameters of all other entries in the same row on the same wall of the box. Again assuming your four three-inch and one two inch are all in a row, (6 x 3) + (3 x 3) + 2 = 29 inches minimum tall. I would use a 30 x 30 x 6 box. Remember that the conduit holes into the building must be in the top of the back section of the box. How do you intend to maintain the rainproofness of the box? Raintight hubs? Five "mogul" LB conduit bodies might be a better option.