It does make a difference on what circuits are in the box, power/lighting or intrinsically safe?
What type of conduit?
You should consider purchasing a copy of NFPA 820:
NFPA 820 Standard For Fire Protection In Wastewater Treatment And Collection Facilities, 2020 Edition
"This standard shall establish minimum requirements for protection against fire and explosion hazards in wastewater treatment plants and associated collection systems, including the hazard classification of specific locations and processes."
With respect to your diagram and this additional description, the equipment and wiring methods must be consistent with Section 501.10(A), especially Section 501.10(A)(3.) This ultimately means the box must be explosionproof unless it meets one of the other recognized protection techniques listed as suitable for Class I. Division 1 in Section 500.7. To be honest, unless is Intrinsically Safe or Purged/Pressurized, then Explosionproof is your most likely choice. That said. it will need to be sealed per Section 501.15(A)(1)(2).Type of conduit: 2" pvc coated conduit with seals.
Circuits: Power for field equipment.
Does this application require the enclosure to be explosion-proof/type 10?
With respect to your diagram and this additional description, the equipment and wiring methods must be consistent with Section 501.10(A), especially Section 501.10(A)(3.) This ultimately means the box must be explosionproof unless it meets one of the other recognized protection techniques listed as suitable for Class I. Division 1 in Section 500.7. To be honest, unless is Intrinsically Safe or Purged/Pressurized, then Explosionproof is your most likely choice. That said. it will need to be sealed per Section 501.15(A)(1)(2).
BTW, sealing nonexplosionproof enclosures is generally useless in hazardous locations.
Downstream barriers do not create an intrinsically safe condition inside the box.Just looking for some clarification...
So, if the circuits downstream have intrinsically safe barriers on them, does the junction box in the classified area require an explosion-proof enclosure?
unless it is pressurized.BTW, sealing nonexplosionproof enclosures is generally useless in hazardous locations.