racerdave3
Senior Member
- Location
- Western Massachusetts
Hi folks, I have a question about junction box sizing. I have a job where I have underground conduit (1 1/2" PVC) going out to a gargage, and where it comes into the house, I am going to land a junction box and then run SER cable (3 conductor with ground) back to the main service panel. My question deals with the size of the box I will need. I know I have looked in the code book and 314.16 (A) and (B) deal with standard size boxes and conductors as large as #6. Further on in 314.28 they talk about junction box sizing and by the information in this article, it would appear that I would need a box that is 6 times the largest conduit, in this case being 1 1/2", meaning the box would need to be 9" inches, thus a 10 x 10 would work. Am I missing anything here? Also, if the 10 x 10 is the box required by code, what about depth? Is 4 inch ok or more needed? I will of course be splicing the conductors in this box, using connectors suitable for cu/al that keep the conductor separate, NO SPLIT BOLTS in this application. I do have limited space in the area of the basement where this box will be, so I am trying to keep the box as small as I can and stay code compliant. Thank you.