Is there an NEC requirement limiting the number of terminal strip connections at 2-connections per terminal or is this just a good "Rule of Thumb"?
Is there an NEC requirement limiting the number of terminal strip connections at 2-connections per terminal or is this just a good "Rule of Thumb"?
Terminals are only rated for 1 wire, unless listed otherwise.
110.14( A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
And if the terminal block is internal to the equipment and not used for connecting field wiring, then the NEC might not have much to say about it in the first place.
You will have to look at the manufacturer's information as some terminal blocks are suitable for use with more than one conductor per terminal point.