B boblhead Member Location New Hampshire Occupation Electrician Dec 29, 2024 #1 Unclear on exterior trough size, 6- 11/2” conduits entering on bottom, 6 #2 ser cables entering on back (adjacent) wall for transition splicing
Unclear on exterior trough size, 6- 11/2” conduits entering on bottom, 6 #2 ser cables entering on back (adjacent) wall for transition splicing
Dsg319 Senior Member Location West Virginia Occupation Wv Master “lectrician” Dec 29, 2024 #2 Without calculations I’d go at least 10x10. Save the blood knuckles.