I have an application in a CL. 1 Div. 1 Gr. C,D area, in a enclosure I only have one strip on terminal blocks
as the terminal are not arcing or sparking devise
would a NEMA 4X enclosure be permitted or would I need an NEMA 7 enclosure with seals
I understand that the enclosure must be rated for the area classification is this the reason to install a NEMA 7 enclosure only
and were in the code would I find this information if a NEMA 7 enclosure is required for terminal blocks
I realize that the AHJ would have final decision
thanks
as the terminal are not arcing or sparking devise
would a NEMA 4X enclosure be permitted or would I need an NEMA 7 enclosure with seals
I understand that the enclosure must be rated for the area classification is this the reason to install a NEMA 7 enclosure only
and were in the code would I find this information if a NEMA 7 enclosure is required for terminal blocks
I realize that the AHJ would have final decision
thanks