kwired

Electron manager
Location
NE Nebraska
Remember if it is a metal box with metal raceways attached that are considered equipment grounding conductors then the box is already grounded. This does not relieve you from connecting equipment grounding conductors to the box if there are splices or terminations within the box. 250.48. Isolated grounding conductors are the exception.
 

squaredan

Senior Member
Location
Pennsylvania
. This does not relieve you from connecting equipment grounding conductors to the box if there are splices or terminations within the box. 250.48. Isolated grounding conductors are the exception.[/QUOTE said:
I dont have a 250.48(2008NEC) did you mean 250.148 or are you working out of the 2011NEC?