Bjenks
Senior Member
- Location
- East Coast of FL
I believe I have found the problem to a customer?s electrical issue. They ran power out to the 3 fingers of a marina underneath the dock and had some pull boxes installed 20 years ago. It looks like they are NEMA 3R and I believe water has gotten in and started to corrode the spices.
This is a fixed pier and the junction boxes are for feeders and obviously below the electrical datum line. Looking at NEC 2008 555.9 says to use from what I can tell NEMA 6P enclosures only. However, it seems to say you can use junction boxes for floating piers only. Does anyone else get this or am I miss-reading it? I think NEMA 6P is the only acceptable box to meet the code, would you agree?
This is a fixed pier and the junction boxes are for feeders and obviously below the electrical datum line. Looking at NEC 2008 555.9 says to use from what I can tell NEMA 6P enclosures only. However, it seems to say you can use junction boxes for floating piers only. Does anyone else get this or am I miss-reading it? I think NEMA 6P is the only acceptable box to meet the code, would you agree?