Junction Boxes

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I need to relocate a 200 amp panel in a single family home. There are probably about twelve NM cables that will be too short to reach the new panel location. The carpenter doesn't want me to use the old panel as a splice box, but would like me to install a junction box above a suspended ceiling. I'm assuming to size the junction box I need to find the cubic inches of all of the NM cables and then find a box that can handle that amount (L x W x H). For the ground wires, can I just install a ground bar? Am I on the right path with this?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You can use one large box or several 4" or 4-11/16" boxes.

Yes, you can use a ground bar, or pigtails and wire-nuts.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Often times a short raceway nippled to your new panel will make a neat installation in these situations
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm doing a similar installation now. I'm using an 8x8 screw cover box with two EMT nipples.
 