Junction / Pull Box sizing
kpepin
On a pull box, if I plan on running conduits out of 3 sides, what is the proper method of sizing the box.
example:
All 1" conduits
5 conduits in side A
3 Conduits in side B (straight through)
2 Conduits in side C (90 degrees from A and B)
Do I use 8"+2" = 10" for the 3 that go straight through and 6"+1"= 7" for the 90 degree pull and just use a 10" x 10" box or is there anything else I need to consider? (I would probably use a 12"x12" instead of 10"x10" if 10" was minimum)
Re: Junction / Pull Box sizing
kpepin,if conductors are 4AWG or larger:314.28
8 x 1 = 8" = on A&B (straight)
6 x 1=6+1=7" on C angle (90 degree)
8 x 8 minumum box (keep in mind of deflection
on the angle pull between the 1" conduits)
If conductors are smaller than #4AWG
see table 314.16(b)cubic inches
[ January 29, 2005, 02:08 AM: Message edited by: dillon3c ]
For some reason I thought you added the sum of all other trade sizes for straight pulls on top of the x8 multiplier. Thanks.
314.28(a)(1) Straight Pulls In straight pulls, the length of the box shall not be less that Eight times of the largest raceway....(No other additions required on a straight pull)