Just a few questions
joeyww12000
Chatsworth GA
Could someone explain to me conduit fill and code that states no more than 3 current carrying conductors in a raceway. On the conduit fill charts you are shown alot more conductors in a conduit than 3. Im sure there is an explanation that makes sense. I would just like to get a better understanding of how to come up with correct amount of circuits in my conduit other than taking someone elses word for it. I know bigger pipe usually means bigger wire not more wires, but I see alot of 3/4 emt upgraded to 1 inch just to be filled up with #12 wire and I know you shouldnt do it. I would appreciate your input.
You can put as many conductors in a raceway as the fill charts show.
However as soon as there are more then 3 current carrying conductors in a raceway you have to derate (reduce the rated ampacity) of the conductors.
You can put more than three in the conduit. You just can't use them to their full capacity. You must derate the ampacity of the current carrying conductors according to table 310.15(B)(2)(a)
Edited... I may not be good, but I'm slow.
Dennis Alwon said:
Look at T 310.15(B)(2)(a). You can have 20 wires in a conduit-- you just need to derate after 3 CCC
Yeah, what they said! :D