So what’s going on,
You know the electrical panel you installed a couple of years ago, and we are trying to install a sub- panel to it , when we did all our upstairs lights in our new addition we are building started to flicker
Mam, how did you get my name?
Your name was on the electrical panel on a green sticker
Oh, I am the electrical inspector that did a re-meter inspection on your service a couple of years ago
I left the house to look at what they had going on, I get there and they tell me they have been fallowing advise they received from the big box store
Base board heaters to three bed rooms 240 volts, three bedrooms, three circuits everything in the three bedrooms on three 20 amp 240 volt circuits
Neutral equipment ground ran to same neutral bus sub- panel,
Hit a basement keyless on the way to second floor addition, hot wire to silver screw, neutral wired to gold screw, concrete basement floor
Will make many happy here, no arcfault breakers
Junction in wall not dry walled yet but was going behind finished drywall
14 awg for stairway three way; was going to be on 20 amp circuit
I hate baseboard heat for bedrooms with little children, but can’t say it’s against code
Hopefully they end up with smoke/carbon detectors
Edit, no tamper resistant rec
You know the electrical panel you installed a couple of years ago, and we are trying to install a sub- panel to it , when we did all our upstairs lights in our new addition we are building started to flicker
Mam, how did you get my name?
Your name was on the electrical panel on a green sticker
Oh, I am the electrical inspector that did a re-meter inspection on your service a couple of years ago
I left the house to look at what they had going on, I get there and they tell me they have been fallowing advise they received from the big box store
Base board heaters to three bed rooms 240 volts, three bedrooms, three circuits everything in the three bedrooms on three 20 amp 240 volt circuits
Neutral equipment ground ran to same neutral bus sub- panel,
Hit a basement keyless on the way to second floor addition, hot wire to silver screw, neutral wired to gold screw, concrete basement floor
Will make many happy here, no arcfault breakers
Junction in wall not dry walled yet but was going behind finished drywall
14 awg for stairway three way; was going to be on 20 amp circuit
I hate baseboard heat for bedrooms with little children, but can’t say it’s against code
Hopefully they end up with smoke/carbon detectors
Edit, no tamper resistant rec