90.2(B)Not Covered. This Code does not cover the following:
(5) Installations under the exclusive control of an electric
utility where such installations
a. Consist of service drops or service laterals, and as-
sociated metering,
Around here that drop would not be covered by the NEC.
Around here that drop would not be covered by the NEC.
This is also reaffirmed some by the change in Art 100 definitions in 2011 for the terms service drop, service lateral, service point.
If those conductors are on the POCO side of the service point, the NEC does not apply to them.
Here we go by 225.19
I don't make the rules, I just follow them.
I thought the weatherhead was supposed to be above the clevice.