Suppose I had a couple of 200 HP 480V motors.
Code allows the short circuit protection to be 250% or 600A.
Any reason I actually have to have a CB on each motor? Can't I just use the main CB in the panel and buy a 600A CB and feed both motor starters off the same CB? Its maybe an odd group motor installation but it seems to fit the bill.
Code allows the short circuit protection to be 250% or 600A.
Any reason I actually have to have a CB on each motor? Can't I just use the main CB in the panel and buy a 600A CB and feed both motor starters off the same CB? Its maybe an odd group motor installation but it seems to fit the bill.