Proposed set up for our new testing facility: 2.5MVA 480V utility transformer feeding our 2.5MVA 600V transformer (utility does not offer 600V transformers) to power our loads including 1800kW of non-linear VFDs loads. These VFDs create typical harmonics (about 35% I THD, 8% V THD). My understanding is that utilities don't offer transformers with k-factor rating.
- Does oversizing the 480V transformer compensate for its lack of k-factor rating?
- How about passive harmonic filter to mitigate the harmonics? Filter can have a contactor that closes at higher loads to avoid creating leading power factor on utility transformer.