7- 16 - (324-4): Reject
SUBMITTER: Larry Seekon, Minneapolis Electrical Inspections Department
COMMENT ON PROPOSAL NO.: 7-22
RECOMMENDATION: Reject the proposed revision.
"or in the hollow spaces of walls, ceilings and attics when such spaces as insulated by loose or rolled insulation material."
SUBSTANTIATION: No factual substantiation of dangerous overheating has been submitted to justify prohibiting loose or rolled insulation material in contact with concealed knob and tube wiring. I am not aware of fires due ONLY to insulation touching knob and tube wiring. However fires do occur because of overfusing and improper splicing or tapping of these circuits. These hazardous conditions are already Code violations.
In the colder regions of the United States there are many thousands of homes now existing with loose or rolled insulation in contact with concealed knob and tube wiring. Most current building codes require the insulation to be fire retardant.
To comply with such a restriction would result in a substantial increase in the cost of rewiring existing homes. New wiring would have to be fished in or surface raceway would have to be installed to replace existing knob and" tube wiring. Both of these methods are very labor extensive and would substantially increase the cost of rewiring. Many people also object to the installation of surface raceway in the nicely decorated homes. In many circumstances, it would be very difficult if not impossible without damaging the walls or ceilings, for an electrical inspector to determine if insulation
material had been installed.
I am very apprehensive of what a judge would think about an inspector issuing an elderly widow on Social Security an order to eliminate all concealed knob and tube wiring in contact with loose or rolled insulation, especially when the home was reinsulated ten years ago
and there have been no electrical problems.
I foresee many enforcement problems if the proposed revision is accepted.
PANEL ACTION: Reject.
PANEL COMMENT: The Panel wants to reaffirm its previous action and to inform the submitter that it is not the intent to make this change retroactive.
VOTE ON PANEL ACTION:
AFFIRMATIVE: 10
NEGATIVE: Roberts.
EXPLANATION OF VOTE:
ROBERTS: The Panel Action to reject this comment will require that concealed knob and tube wiring installations in older homes be replaced i f , in the process of insulating the home, the wiring becomes embedded in insulation. The Panel has no substantiating evidence to reject this comment. The substantiation stated in Comment 7-16 is correct. Concealed knob and tube wiring systems in thousands of residences are now embedded in insulation and no overheating problems have been reported