The following information I received from the utility company
The fault Current for this project is as follows:
Phase – Phase = 9693 Amps
X/R Ratio: 1.2
I specified the KAIC to be 10KAIC, since the rating should be higher than the available fault current.
But when I got the submittal for the EC, it specified the MDP to be 42 KAIC.
Will the system still work if the other breakers installed in the Panel are 10 KAIC.