Guys,
Good Day!
I just want to seek expert advice regarding the KAIC rating of a Busduct Plug-in Circuit breaker. My calculated 3phase bolted fault current at the line side of the plugin cb (PICB) is 34.3kA, now the contractor purchased a 35kAic PICB. Is it still acceptable? Are there some safety factor needed, let say KA x 1.25?
thanks,
AAEB
Good Day!
I just want to seek expert advice regarding the KAIC rating of a Busduct Plug-in Circuit breaker. My calculated 3phase bolted fault current at the line side of the plugin cb (PICB) is 34.3kA, now the contractor purchased a 35kAic PICB. Is it still acceptable? Are there some safety factor needed, let say KA x 1.25?
thanks,