Hello. I am sizing a panel a 800 amp 277/480 service. My question is how do I rate the panel for kaic. My largest breaker the main is rated for 65kaic or aic for SD breakers. Do I rate it the same as the breaker kaic rating.
The short answer is that the transformer's KVA, impedance, and secondary voltage are the main factors determine the available fault current (AFC), which the KAIC needs to meet or exceed. The upper limit for AFC from a transformer is (amps associated with KVA) divided by the impedance as a decimal.
The long answer is that available fault current on the primary side of the transformer can influence this value as well, and mean that the AFC on the secondary is less than that. Also, the impedance of conductor routes can also reduce this. Also, motor loads can contribute their own fault current to the total. It is recommended to get the available fault current at the service point, and then add in any motor contribution fault current, to get what the total AFC is at any given point in the system. There are fault current calculators (aka short circuit current calculators) that allow you to model all the factors that come in to play.
Terminology:
AFC = Available fault current is the maximum current that could realistically occur at a given position in your service.
KAIC is kilo amps interrupting capacity, which is the maximum amps that a breaker can withstand and trip safely without catastrophically failing.
KAIR is the equivalent term for fuses.
SCCR is short circuit current rating, which is the maximum amps that any other device in the system could withstand, and usually applies to equipment that isn't an OCPD, such as panelboards, disconnects, and meter sockets.
Ultimately, the values of KAIC, KAIR, and SCCR must meet or exceed the available fault current, unless combinations of devices with listed series ratings allow you to take credit for upstream devices protecting downstream devices.