In reveiwing a set of plans for a 5 story building I have come across the following dilemma
Local power company sez we need 100,000 amp interrupting capacity
The MDP is rated at 65KAIC.
The panels downstream of it are rated at 10KAIC
The specs say breakers are to be 14KAIC
The building will have a Standby Gen. due to the need for a Fire Pump and Accessable Elevator,hence selective coordination applies (Article 701)
It seems to me that a short on a branch circuit could damage the breaker and associated panel and not properly clear until the MDP opens or something downstream of it blows up or catches fire.This also just wrecks any thoughts of selective coordination like the fire pump working to put out the fire that probably just hapenned.
Am I on the right track here?????
Local power company sez we need 100,000 amp interrupting capacity
The MDP is rated at 65KAIC.
The panels downstream of it are rated at 10KAIC
The specs say breakers are to be 14KAIC
The building will have a Standby Gen. due to the need for a Fire Pump and Accessable Elevator,hence selective coordination applies (Article 701)
It seems to me that a short on a branch circuit could damage the breaker and associated panel and not properly clear until the MDP opens or something downstream of it blows up or catches fire.This also just wrecks any thoughts of selective coordination like the fire pump working to put out the fire that probably just hapenned.