If I have an exisitng 200a 240v 3 ph 65kaic panel and I wanted to add a 100a subpanel off the 200a do i need to stay at 65Kaic or better or can I go down 22kaic.
I would like to make a few points.If I have an exisitng 200a 240v 3 ph 65kaic panel and I wanted to add a 100a subpanel off the 200a do i need to stay at 65Kaic or better or can I go down 22kaic.
Thank you for reply, You are The MDP is a GE 800a with 3- 200a GE panel series AQF type these panels are 65kAIC and 1-100a GE type AQF panel 65kaic rating . The drawings indicate that the new subpanel will extend off the 100a and match name and KAIC rating. There is no added load. They are just relocating circuits to isolate equipment breaker to one panel, I dont know why but that the long and short of story. If this was not the case, how would one proceed to add a sub panel and keep series rated? Would I keep AIC from breaker rating to new subpanel or keep the kaic from panel its feedting?I would like to make a few points.
First, one thing we would need to know is more specifics about what "65 kaic panel" means. The panelboard itself has a SCCR rating, while the breakers have an AIC rating. In practice, a panel board will likely have a SCCR as high or higher than the AIC of the highest rated breaker that can go in it, so this is mostly academic I believe. Are all the branches 65k? It's quite rare to have 65k branches because of series ratings - but I guess fully rated systems become more common in industrial settings or where there is motor contribution as petersonra mentioned.
It's hard to know without some digging if the 65k is actually needed. It seems a fair number of people use 65k mains because they don't know how or are unwilling to investigate the available fault current. Or perhaps they just want to be covered for future expansion. 65k branches are rare in my world, and expensive* too, so it seems unlikely someone would use them Willy nilly.
Many times you just don't have to worry about interrupting ratings in downstream equipment, due to series ratings. Of course the downstream equipment has to have a series rating with the upstream equipment, but it usually will if it's the same brand and not something old and obsolete. One other thing to note, 200A frame 65kaic breakers will usually series rate all the way down to 10k branches. However 400 amp frame breakers usually will not. Of course if you have some sort of spec that states q certain interrupting rating, you have to do what it says even if not needed.Thank you for reply, You are The MDP is a GE 800a with 3- 200a GE panel series AQF type these panels are 65kAIC and 1-100a GE type AQF panel 65kaic rating . The drawings indicate that the new subpanel will extend off the 100a and match name and KAIC rating. There is no added load. They are just relocating circuits to isolate equipment breaker to one panel, I dont know why but that the long and short of story. If this was not the case, how would one proceed to add a sub panel and keep series rated? Would I keep AIC from breaker rating to new subpanel or keep the kaic from panel its feedting?