Our AHJ is now requiring the use of a "kenny clamp" for GEC. What alternative products are available? Also, if there are two GECs (water bond, ground rods) then I assume two kenny clamps are required?
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
Our AHJ is now requiring the use of a "kenny clamp" for GEC. What alternative products are available? Also, if there are two GECs (water bond, ground rods) then I assume two kenny clamps are required?
What are they?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
There is no reason to use a clamp for a GEC except to line the manufacturers pockets, I know that doesn't help with an overzealous inspector or AHJ. Before I would buy a Kenny Clamp that has been deceptively marketed to be a code required item I would sleeve the GEC in PVC.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Roger they are not required by the NEC. If you use them then it has to be with the listing of the Kenny clamp which tells you the size and number of conductors permitted.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I've never used a Kenny Clamp but from the data sheet it appears you might be able to use one at the end of a metallic conduit to satisfy 250.64 (E) without a bond bushing/bond jumper.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'm an ignorant Brit but what is that..........?
The GEC (grounding electrode conductor) from the system grounding comes out of the meter or panel. We are required to provide a way for utilities to attach their ground to the system ground. The item shown allows the GEC to go through it and is clamped by a screw. The other screws are ports for other ground wires to connect to. It is called an inner system bonding bridge.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There is no reason to use a clamp for a GEC except to line the manufacturers pockets, I know that doesn't help with an overzealous inspector or AHJ. Before I would buy a Kenny Clamp that has been deceptively marketed to be a code required item I would sleeve the GEC in PVC.
This issue with the Kenny Clamp has come up before, The general consensus here is that it’s not required.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
The GEC (grounding electrode conductor) from the system grounding comes out of the meter or panel. We are required to provide a way for utilities to attach their ground to the system ground. The item shown allows the GEC to go through it and is clamped by a screw. The other screws are ports for other ground wires to connect to. It is called an inner system bonding bridge.
Thank you, Sir!
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Didn't we run into this before with an inspector making the electricians use kenny clamps. Probably the same guy who got fired from his last job and ended up where the op lives. hahaha
 