anndee4444
Member
- Location
- California
I am stuck in a battle with Kern County (California) over their interpretation of 705.12(D), and am hoping that someone might have ideas on other ways to get them to agree with my interpretation. I am attempting to use this section to get out of the (D)(1) through (D)(7) requirements, specifically the 120% rule.
I have also tried arguing that if the definition of 'Feeder' is "circuit conductors between the service equipment... and the final branch-circuit overcurrent device.", then Feeders should mean multiple devices. They did not like this either. :thumbsdown: They gave the excuse that 'Feeder' is never used in the code (it is... 474 times. Feeders is used 239 times)
I have contacted the California Building Standards Commission, who referred me to the Office of the State Fire Marshall. I am waiting for a call back right now, but even if I do get OSFM to agree with my interpretation, Kern County does not have to agree.
Does anyone have any ideas of how I can get them to agree with my interpretation? Is my interpretation incorrect?
Where distribution equipment, including switchgear, switchboards, or panelboards, is fed simultaneously by a primary source(s) of electricity and one or more utility-interactive inverters, and where this distribution equipment is capable of supplying multiple branch circuits or feeders, or both, the interconnecting provisions for the utility-interactive inverter(s) shall comply with 705.12(D)(1) through (D)(6).
Our equipment is NOT capable of supplying multiple branch circuits, and not capable of feeding multiple feeders. Kern County's interpretation of this section is that 'multiple' does not apply to 'feeders' (only branch circuits). I have tried explaining that if this was the intent of the code, there would be an additional comma after 'multiple branch circuits'. They didn't like this. :thumbsdown:
I have also tried arguing that if the definition of 'Feeder' is "circuit conductors between the service equipment... and the final branch-circuit overcurrent device.", then Feeders should mean multiple devices. They did not like this either. :thumbsdown: They gave the excuse that 'Feeder' is never used in the code (it is... 474 times. Feeders is used 239 times)
I have contacted the California Building Standards Commission, who referred me to the Office of the State Fire Marshall. I am waiting for a call back right now, but even if I do get OSFM to agree with my interpretation, Kern County does not have to agree.
Does anyone have any ideas of how I can get them to agree with my interpretation? Is my interpretation incorrect?