We had a inspection last week, for a small job. We ran a 15a 125V multiwire circuit from a warehouse to an outbuilding for lts. and receptacles. One circuit was for lts, one for receptacles. #12 THHN, 2 hots, 1 nuet., 1 GRND.
I was in a hurry to finish, and forgot to put in the disconnecting means for the outbuilding. I had planned to use a double pole single throw switch, 20A rated for this. I was onsite the day of inspection installing this switch when the inspector showed up, and I explained to him what I was doing.
He failed me, I asked for code ref. and he replied 225.30. He wants a sub panel with a main, and branch circuit breakers in the outbuilding.
I read NEC as I can have two circuits in outbuilding so long as they are multiwire branch ckt. MET 225.30 I also have met 225.31 with my switch, am I missing something here?????
Oh yeah, Inspector is about 80 yrs old to......stubborn old cuss....
I was in a hurry to finish, and forgot to put in the disconnecting means for the outbuilding. I had planned to use a double pole single throw switch, 20A rated for this. I was onsite the day of inspection installing this switch when the inspector showed up, and I explained to him what I was doing.
He failed me, I asked for code ref. and he replied 225.30. He wants a sub panel with a main, and branch circuit breakers in the outbuilding.
I read NEC as I can have two circuits in outbuilding so long as they are multiwire branch ckt. MET 225.30 I also have met 225.31 with my switch, am I missing something here?????
Oh yeah, Inspector is about 80 yrs old to......stubborn old cuss....