A problem I was presented in class. The minimum kilovolt-amperes of a generator that will be required to start simultaneously, two 7.5 horsepower, 3 phase, 230-volt, Code letter F motors.
So I know that to find the minimum kilovolt-amperes you go to Code Letter F for the Locked-Rotor Code letters. Code Letter F=5-5.59
I know you are supposed to then take the lesser of the two numbers(5) and multiply by the horsepower, so the answer would be.
5(Code letter F)*7.5HP=37.5
Then because their are two motors you multiply the result by 2
37.5*2=75
75 kilovolt-amperes.
The question I am uncertain of is.
The minimum kilovolt-amperes of a generator that will be required to start two selectively controlled 7.5 horsepower, 3-phase, 230-volt, Code leter F motors is?
Selectively controlled, does this mean I count the motor as 1 so because the motors are selectively controlled would the calculation just be
5(Code letter F)*7.5HP=37.5 kilovolt-amperes per horsepower
So I know that to find the minimum kilovolt-amperes you go to Code Letter F for the Locked-Rotor Code letters. Code Letter F=5-5.59
I know you are supposed to then take the lesser of the two numbers(5) and multiply by the horsepower, so the answer would be.
5(Code letter F)*7.5HP=37.5
Then because their are two motors you multiply the result by 2
37.5*2=75
75 kilovolt-amperes.
The question I am uncertain of is.
The minimum kilovolt-amperes of a generator that will be required to start two selectively controlled 7.5 horsepower, 3-phase, 230-volt, Code leter F motors is?
Selectively controlled, does this mean I count the motor as 1 so because the motors are selectively controlled would the calculation just be
5(Code letter F)*7.5HP=37.5 kilovolt-amperes per horsepower