Kitchen exhaust fan circuit

Status
Not open for further replies.

vanetten

Member
Can I connect a kitchen exhaust fan from a above counter gfci circuit?

The exhaust fan load is approx. 240W
 

jtester

Senior Member
Location
Las Cruces N.M.
Re: Kitchen exhaust fan circuit

I need more info before answering the question. Is this a residence, is the circuit you are connecting to a small appliance branch circuit as outlined in 210.11.(C)(1)?
In a residence, most of the time, you can't connect an exhaust fan to the small appliance circuits.

Jim T
 

vanetten

Member
Re: Kitchen exhaust fan circuit

Is this a residence....yes

is the circuit you are connecting to a small appliance branch circuit as outlined in 210.11.(C)(1)?
yes
 

vanetten

Member
Re: Kitchen exhaust fan circuit

can I connect the exhaust fan to a lighting circuit or refrigerator circuit?
 

electricmanscott

Senior Member
Location
Boston, MA
Re: Kitchen exhaust fan circuit

Depends how you connect it. If it is cord and plug connected it must be an individual branch circuit serving only the hood. If it is hardwired it can be on the lighting circuit but it can not be on the fridge circuit.
 

allenwayne

Senior Member
Re: Kitchen exhaust fan circuit

As a standard we dedicate the hood circuit .Most
of the time there is a hood/micro,also use it for range ignitor recep. in a gas community.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Kitchen exhaust fan circuit

Originally posted by allenwayne:
Most of the time there is a hood/micro, (we) also use it for range ignitor recep. in a gas community.
Remember Allen, as Scott said, under the 2005 we can no longer use the "Hood" circuit for any other outlet if the hood is cord-and-plug-connected. Little bitty ignitor included.

I would put the outlet for the igniter on the countertop GFI circuit--that's still allowed. :roll:
 