AndrewG185
Member
- Location
- Chalfont, PA
I swear I searched first, these forums and the web as well as scouring NEC rules; if this is covered somewhere drop a link. I'm looking for some clearing up on E3703.2 which states that the kitchen counter top receptacles shall be served by a minimum of two 20-ampere-rated branch circuits, either or both of which shall also be permitted to supply other receptacle outlets in the same kitchen, pantry, breakfast and dining area including receptacle outlets for refrigeration appliances. O.k., no problem. What I am unsure of is whether this is stating that a counter top has to have both GFI circuits over it. For example, is it acceptable for me to have 1 of my GFI protected circuits serving the main counters and the other serving the kitchen island? My inspector came in and failed me today saying I have too many receptacles on a GFI (8), and that I am required to have 2 circuits serving the counter tops. I asked him to cite me the code that I had violated and he pointed to E3901.4.2 on my plans(wrong). I told him that was code for outlets required on the island and he said he'd get back to me. He later emailed me that I violated E3703.2. I asked him to cite the code that dictates how many outlets I can have downstream from a GFI, he never responded. I don't know whether he is arguing that I have too many receptacles or that I have not provided enough circuits. I'm not here saying he is wrong, just that I have never had an inspector tell me this in 40+ kitchens I've installed. Can anyone help me out with this? Do I have too many receptacles on 1 GFI? Again, if this is covered please just post a link...first time poster here!! Thanks everyone.