Kitchen GFI receptacle circuits

Status
Not open for further replies.

alvez

Member
Has anyone taken a 12-3 w/gnd for the two required kitchen utilitiy circuits and protected them on a
double pole 20 amp. GFI circuit breaker. I'm suspicious
it won't work since the GFI reads the differential between
hot and neutral! Am I right?
 

iwire

Moderator
Staff member
Location
Massachusetts
It will work as long as all three circuit conductors (White, Black, Red) are terminated to the two pole GFCI breaker.

But of course a problem on one circuit will take out both circuits.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I'm suspicious it won't work since the GFI reads the differential between hot and neutral!
A double pole GFCI breaker will look at the current on both hots and the neutral. Without leakage or a fault this current will always sum to zero, so the two pole breaker works for both 240 volt loads and 120 volt loads as well as any combintation of the two.
Don
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Although it will work with a 2P CB, is this more cost effective than 2 GFCI receptacles? Not to mention the downside of having two circuits trip at once.
 

Limey Pete

Member
Location
Tampa Florida
infinity said:
Although it will work with a 2P CB, is this more cost effective than 2 GFCI receptacles? Not to mention the downside of having two circuits trip at once.

You forgot to add that if you went this route then 12/3 would NOT work. it would have to be 2 x 12/2

BEFORE Anyone comments; I take that all back. A long day with little sleep tonight. Sorry
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Limey Pete said:
You forgot to add that if you went this route then 12/3 would NOT work. it would have to be 2 x 12/2

Why is that? If you use two sp breakers with a MWBC , then you could hook one GFI receptacle at that point and run a 12/2 to the next box hooking the neutrals ahead of the GFI. It will work.
 

Limey Pete

Member
Location
Tampa Florida
Dennis Alwon said:
Why is that? If you use two sp breakers with a MWBC , then you could hook one GFI receptacle at that point and run a 12/2 to the next box hooking the neutrals ahead of the GFI. It will work.

Yup! and if you read my "edit" closely you will see that I can't even tell the difference between "tonight" and "last night" right now. Told you I was tired.
 

celtic

Senior Member
Location
NJ
danickstr said:
just out of curiosity, is there any advantage to this setup, other than a customer not wanting to look at gfis?

The customer may get some extra exercise :)
 

stickboy1375

Senior Member
Location
Litchfield, CT
celtic said:
The customer may get some extra exercise :)


If the panel is anywhere but in the kitchen....;) I can't ever remember resetting a gfi in my own home... just trouble calls, I just don't understand why people cannot understand how to reset a breaker or a gfi? I clearly explain to my customers how to do it before I leave....
 
Status
Not open for further replies.
Top