Our electrical engineering involves mostly school and most of the schools have kitchens. I visited one of the sites with the contractor who brought to my attention a problem which he hoped I could resolve.
A double wide freezer was pluged into a double wide reachin freezer. Our drawings indicated a 20 amp GFI for the freezer circuit. The GFI tripped causing the food inside to defrost. The school district sent an invoice to the contractor for replacement of the food.
We designed the circuit and specified that all 15 and 20 amp receptacles in the kitchen be GFI type in accordance with 2005 NEC (2007 CEC in California), article 210.8 (B)(2). I told the contractor that there were no exceptions given for kitchen receptacles.
What do we do? The circuit required for the freezer is 20 amps, single phase.